Hi,

We have an NCD PR55-47-2CR 2-channel 4–20 mA receiver connected to two SICK PBT vacuum transducers. Here are some information for context:

Receiver:

  • Firmware 10
  • Battery 3.28 V / 98.56%
  • Radio communication and Node-RED packets are working normally

Current readings:

  • CH1: ADC 665 / 0.45 mA
  • CH2: ADC 676 / 0.46 mA

Both channels are physically connected. I disconnected and reconnected the two M12 plugs, checking their keyed orientation, but the readings did not change.

Since 0.45 mA is also the value we normally see on unused channels, both loops appear open or unpowered.

I will attach some photo for evidence of:

  • Node-RED payload
  • field installation and transmitter photos
  • internal photos of the receiver (ignore the radio MAC visible in the older internal photos, as the radio module was replaced later)

The internal connectors and ribbon cables appear seated, with no visible damage.

What could be the issue?

Thank you!

Hello @davidemagno let me ask you;

  1. Did the sensor send correct current data at any point?
  2. Did you configure any of the sensor parameters?
  3. Could you share how did you perform the connection between the M12 connector and the SICK PBT transducers please?

Hi @Eduardo_Mtz thanks for taking care.

  1. For this specific 2-channel receiver, I have not yet confirmed a valid reading during my recent tests. The installation was already present before I started managing it, so it may have worked correctly in the past, but I do not currently have a verified historical test showing valid 4–20 mA values from these two specific transducers.
  2. No change in default parameters was made. The radio module was replaced previously, and the radio/network settings were restored so that the device could communicate with the gateway again. The receiver is now transmitting normally to Node-RED. Default calibration values are:
  • Low calibration: 68805
  • Mid calibration: 68724
  • High calibration: 68714
  1. Not sure about this point but i can take some picture if needed, what do you need exactly to see? thanks

Hi @davidemagno thank you for the information, I would like to double check the connection between the NCD current loop receiver and your SICK PBT Transducers, how is the connection? what diagram or pin out did you use for connection?

Thank you.

When the sensor reports a reading like this, it indicates that there is a connection issue

Hi @Eduardo_Mtz thanks for the clarification. Hello,

thanks for the clarification.

From the photos attached, the setup is a direct M12-to-M12 connection.

The SICK PBT transducers are factory-terminated M12 devices, and the individual conductors inside the cable are not visible from the outside.

On the SICK side, the sensor body shows the standard pinout marking for the 2-wire current loop connection. I did not use any custom wiring or manual terminal block connection.

At the moment I cannot visually inspect the internal conductors of the cable, but the connectors are keyed and fully seated, so there is no obvious mechanical way to connect them in the wrong orientation

Hi @davidemagno Thank you for the information. You will need to wire a custom connector for this setup. To do so, you can use a cable with an M12 connector on one end and bare wires on the other. I have included a wiring diagram below as an example for your specific use case:

Thank you.

Hi @davidemagno for reference only, this is an example of the cable you should build.

Thank you.

hi @Eduardo_Mtz sorry for the late reply. Just a warning: the diagram you attached looks like a 3-wire sensor example.
My transducers are SICK PBT 2-wire, 4–20 mA devices where both L+ and QA are on pin 1 (brown wire) and M3 go to pin 3 (blue wire). Moreover i would say that the original cabling was done correctly (as i guess it was tested somehow before placing the sensor and cabling). So how could this be solved on 2-wire sensor?

Hi @davidemagno let me share you the diagram for 2-wire sensor (loop powered by NCD Receiver):

Thanks