How to connect 2-wires cables to PR55-53 Interface

Hello,

I have an NCD 2-channel 4–20 mA receiver equipped with a PR55-53 interface , with the following terminals:

V – G – R2 – B – R1 – B

It was previously connected to two SICK PBT 2-wire 4–20 mA pressure transducers, using this wiring: 2x brown wires connected together and then connected to V, CH1 blue wire to R1, CH2 blue wire to R2, white wire connected from G to both B (jumper).

I now need to use CH1 only , disconnecting the second transducer completely.

My understanding is that:

  • CH1 brown wire should remain connected to V.
  • CH1 blue wire should remain connected to R1.
  • CH2 brown and blue wires should be disconnected.
  • The jumper (white wire in photo) between G and the B terminal associated with CH1 should remain connected. But looking at the board i am not sure which B terminal is associated to CH1.

Could you please confirm the correct wiring, particularly which G-to-B jumpers must remain connected when using CH1 only?

I’ve attached photos of the terminal board and existing wiring.

Thank you!

Hello @davidemagno You can use this:

V – G – R2 – B2 – R1 – B1
  • CH1 brown wire to V.
  • CH1 blue wire to R1.
  • The jumper (white wire ) between G and the B1 terminal

Thank you.

ok many thanks! i guess it’s not relevant which B2 terminal i pick from the two available, right?

Hi @davidemagno sorry, I’ve updated the information. For one channel you can use V, R1 and G-B1

1 Like