I am using the 1-Channel Isolated 4-20mA Current Loop Transmitter With Power Supply (PR33-49) I want to control pressure control valve. I measure 36mA output Signal. I dont thinkt the transmitter is malfunctioning I ordered 3 and everytime its the same problem.
I control the loop transmitter with a raspberry Pi.
Any help or advice is greatly appreciated, thanks!
36mA is theoretically impossible give thant its range is limited to 22mA.
- can you measure voltage across the terminals
- can you share a picture of your setup
- are you powering the board using 3.3V or 5V. you should be using 5V.
- RPI does not have any i2c pull ups , so you should be installing on board pull up jumpers
- remove any connection from the board and measure current across the two terminal as well.
- Yes I am Powering the board with 5V
- What do you mean with install Pull up jumpers?
- the output ist 36mA
you need this rpi shield
https://store.ncd.io/product/i2c-shield-for-raspberry-pi-3-pi2-with-outward-facing-i2c-port-terminates-over-hdmi-port/
Hmm Okay… but this device does the same like i did with the jumper wires? it is just connecting the RPI with the current loop transmitter…
Im also not sure what exactly the I2C Adress Jumper does und the Pull-Up Jumpers?
RPI i2c is 3.3v and the 4-20mA board runs at 5V.
Yes, thank you that seems to be the problem… Does the rpi shield you recommended solve the problem?